Usage of Test Lamp - TL3000
본문




[Usage]
1. Turn the test lamp toward Target flame detector.
2. Press operation switch ON [with appropriate operation, the light will blink]]
3. Direct the brightest part of light toward flame detector.
4. Wait for the Flame Detector's activation.
5. If the flame detector does not work properly, repeat guided step from 1 to 4 listed above,
after adjust distance and angle.
6. Press operation switch('OFF')
※ Cover range and activation time depend on manufacturer and model.
Normally 10~15 sec activation time is required within 4m test distance.
7. After the usage, please charge TL3000.(operation switch must be set off during recharging)
[Influence factors for the operation distance]
• Manufacturer & window's contamination status.
• Charging status of the Test lamp.
• At the front side, the longest operation distance will be generated for the Test lamp.
• Must Keep it clean all the time
[Caution]
• Do not look at the light from Test lamp directly.
• Do not use any charger except one provided by Rezontech.
• Do not use during charging.
• The main power will be shut down when TL3000 detects 20V under low voltage and other failure.
• Charging will recover from circuit and battery failure
• RFD-3000, RFD-3000x Only
1. Turn the test lamp toward Target flame detector.
2. Press operation switch ON [with appropriate operation, the light will blink]]
3. Direct the brightest part of light toward flame detector.
4. Wait for the Flame Detector's activation.
5. If the flame detector does not work properly, repeat guided step from 1 to 4 listed above,
after adjust distance and angle.
6. Press operation switch('OFF')
※ Cover range and activation time depend on manufacturer and model.
Normally 10~15 sec activation time is required within 4m test distance.
7. After the usage, please charge TL3000.(operation switch must be set off during recharging)
[Influence factors for the operation distance]
• Manufacturer & window's contamination status.
• Charging status of the Test lamp.
• At the front side, the longest operation distance will be generated for the Test lamp.
• Must Keep it clean all the time
[Caution]
• Do not look at the light from Test lamp directly.
• Do not use any charger except one provided by Rezontech.
• Do not use during charging.
• The main power will be shut down when TL3000 detects 20V under low voltage and other failure.
• Charging will recover from circuit and battery failure
• RFD-3000, RFD-3000x Only