Preparation before sensor test 

1) Block alarm system 

   The alarm system triggered by detector field test may direct facility employees to stop operation and lead to evacuation.

2) Advanced Approval for cooperation

   Some facilities do not allow fire alarm test during their operation. Pre-approval from site manager is recommended.


Detectors Testing Method 
Flame detector sensors fire, the LED light on detector will blink. 
And the fire alarm to be triggered only after the Flame Detector continuously sensors the presence of fire for given delay time.
Caution: Some facilities with flammable storage do not allow on site flame test.


 2b94ff3f38244881c8b3ec3e68ec610c_1517310466_7249.png

1) Test with lighter

This instant test can be done in short distance of 1-3 meter. The sensitivity set on the detector implies the testing distance



 2b94ff3f38244881c8b3ec3e68ec610c_1517310472_411.png

 2) Test with Butane torch

Torch flame size will directly result the testing distance. The flame detection distance is up to 10 meter


Additionally, torch lamp results bluish flame that has similar entity of hydrogen fire, which is nearly invisible. Hold the torch lamp upside down and swing it around to create unburned flame with color, and it will be helpful for FD to sense fire.


Detector’s alarm trigger condition is based on below factors.

① Sensor sensitivity,

② Delay time,

③ Distance between sensor and flame,

④ Flame size may overcome the distance.

 2b94ff3f38244881c8b3ec3e68ec610c_1517310478_8299.png

 3) Test with Fuel container

Flame detector can be tested with fuel container sized 33CM * 33CM with n-Heptane. Rezontech flame detectors meet KFI regulation and qualified by FM performance approvals.


4) Test with REZONTECH TEST Kit 

Test Lamp is useful where physical fire testing is prohibited.



 
UV/IR TEST LAMP - Detection range : 7m (average)
IR3 TEST LAMP - Detection range: 5m (average)

 

cc5022h2i4.png 

Check the battery status. Press on the power button.

Face the lamp toward flame detector and monitor flame detector’s operation.

 cc5022h2i5.png

Check the battery status. Press on the power button.

Face the lamp toward flame detector and monitor flame detector’s operation.

IR3 long distance TEST LAMP (FS-20)

- detection range : 20m Max

Flame Tester(FS-10) 

cc5022h2i6.png

- Power on the unit. (battery or AC powered)

Warming up time required.

- Power on CHOPPER.

- Face test lamp toward flame detector

- Monitor flame detector's operation.

cc5022h2i7.png

- Locate flame tester(FS-10) within the detection angle and distance.

- Light up nozzle.

- Monitor flame detector's operation.